    Connecting cables for VLF test

    Does anyone have specific literature that says whether you can tie together cables for VLF testing? All I see in IEEE are references to "cable systems" which could be interpreted as either a single cable feeding multiple buildings and splices or 3-phase feeder.

  2. #2
  3. Kalbi_Rob's Avatar
    Kalbi_Rob is offline Experienced Member Pro Subscriber
    Join Date
    Feb 2018
    Location
    Jacksonville, NC
    Posts
    290
    Reputation
    Quote Originally Posted by SecondGen View Post
    Does anyone have specific literature that says whether you can tie together cables for VLF testing? All I see in IEEE are references to "cable systems" which could be interpreted as either a single cable feeding multiple buildings and splices or 3-phase feeder.
    IEEE 400.2 does not state how to separate the cable system, but does give example of unique testing situations, as annotated in the below excerpt:

    In addition, some utilities may have components connected to the cable circuit being measured, e.g., oil-filled switches, that cannot be removed but can influence the test results. Most users of dielectric response techniques choose to measure the entire cable system response that would include the responses from all terminations, cable, and joints within the circuit.


    Multiple companies I have been apart of, have always pushed that VLF testing is essentially a go/no go test that if failed, would require the removal of each component to determine the failed portion. So, testing all phases together would not effect the overall test if they all pass. If it fails, then further testing would be required. Obviously, the overall intention is profit driven vs results driven. It has been accepted by the customer as understandable and never had to retest due to tying the phases together, even after some very heated debates.
    The issue comes up with VLF-TD, where we believe Phases must be separated to produce trending results. Where we have issues is whether to test multiple cables tied together in a circuit (such as A-phase on either side of a transformer with the switch off and testing through the terminations). This is discussed in the excerpt I provided above, and would be best left to the decision of the end-user.

  4. #3
  5. SecondGen's Avatar
    SecondGen is offline
    I push buttons.
    NETA Level III Pro Subscriber
    Join Date
    Jan 2014
    Location
    United States
    Posts
    508
    Reputation
    Quote Originally Posted by Kalbi_Rob View Post
    IEEE 400.2 does not state how to separate the cable system, but does give example of unique testing situations, as annotated in the below excerpt:

    In addition, some utilities may have components connected to the cable circuit being measured, e.g., oil-filled switches, that cannot be removed but can influence the test results. Most users of dielectric response techniques choose to measure the entire cable system response that would include the responses from all terminations, cable, and joints within the circuit.


    Multiple companies I have been apart of, have always pushed that VLF testing is essentially a go/no go test that if failed, would require the removal of each component to determine the failed portion. So, testing all phases together would not effect the overall test if they all pass. If it fails, then further testing would be required. Obviously, the overall intention is profit driven vs results driven. It has been accepted by the customer as understandable and never had to retest due to tying the phases together, even after some very heated debates.
    The issue comes up with VLF-TD, where we believe Phases must be separated to produce trending results. Where we have issues is whether to test multiple cables tied together in a circuit (such as A-phase on either side of a transformer with the switch off and testing through the terminations). This is discussed in the excerpt I provided above, and would be best left to the decision of the end-user.
    Thanks for confirming my suspicions, Rob. I don't see any problem with connecting them together. My ultimate conclusion is that any dispute between the ITA and customer would ultimately be resolved by the end user. If the owner wanted the cables separated it would probably be a separate charge. This is one of those times where testing specifications are absolutely critical.

  6. #4
  7. Join Date
    Jun 2018
    Posts
    23
    Reputation
    Quote Originally Posted by SecondGen View Post
    Does anyone have specific literature that says whether you can tie together cables for VLF testing? All I see in IEEE are references to "cable systems" which could be interpreted as either a single cable feeding multiple buildings and splices or 3-phase feeder.
    You can connect them together but it is really important to check the capacitance of the cable. Because long cables might damage your device.

Subscribe

Share this thread

Related Topics

  1. Replies: 1
    Last Post: March 23, 2021, 02:25 PM
  2. Grounding cables not under test
    By epenland in forum NETA Level 2 Exam
    Replies: 1
    Last Post: February 11, 2021, 01:58 PM
  3. How much spacing should you have when testing cables?
    By cjones09 in forum Safety and Arc Flash Talk
    Replies: 5
    Last Post: September 21, 2015, 02:52 PM

Tags for this Thread

Follow us


Explore TestGuy


NETA Certification Training


NICET Electrical Power Testing


Help and Support




You are viewing the archives. Enjoy new features and join the conversation at wiki.testguy.net