I have a transformers winding resistance:
T1(LV SIDE), 3MVA, 34.5/.480 KV
X1-X0= 0.130 mΩ
x2-x0= 0.408 mΩ
x3-x0= 0.320 mΩ
T2(LV SIDE), 3MVA, 34.5/.480 KV
X1-X0= 0.462 mΩ
x2-x0= 0.442 mΩ
x3-x0= 0.241 mΩ
T3(LV SIDE), 3MVA, 34.5/.480 KV
X1-X0= 0.75 mΩ
x2-x0= 1.200 mΩ
x3-x0= 0.480 mΩ
Are they considered balanced as per NETA standard?
I had been finding and searching for the standards on these transformers.