Generator Conductor Sizing

 Jump to latest post
    #1
  1. Join Date
    Jun 2021
    Posts
    2
    Reputation

    Generator Conductor Sizing

    "The conductor ampacity from the Generator terminals to the first distribution devices containing an overcurrent device must not be less than _____ of the generator nameplate current rating."
    Neither the NETA book, nor the test, cover conductor sizing.

  2. #2
  3. ATurton88 is offline Junior Member Pro Subscriber
    Join Date
    Jun 2021
    Posts
    1
    Reputation
    Quote Originally Posted by JoelHolland View Post
    "The conductor ampacity from the Generator terminals to the first distribution devices containing an overcurrent device must not be less than _____ of the generator nameplate current rating."
    Neither the NETA book, nor the test, cover conductor sizing.
    I would imagine that the answer would be no less then 100% of nameplate current rating. Basically, you wouldn't want to install a conductor that has an ampacity lower then 100% full load of the source.

    If you could post what your answer options were and what you selected I think I would be able to better direct you/understand what the question is looking for.

  4. #3
  5. Kalbi_Rob's Avatar
    Kalbi_Rob is offline Experienced Member Pro Subscriber
    Join Date
    Feb 2018
    Location
    Jacksonville, NC
    Posts
    290
    Reputation
    Quote Originally Posted by JoelHolland View Post
    "The conductor ampacity from the Generator terminals to the first distribution devices containing an overcurrent device must not be less than _____ of the generator nameplate current rating."
    Neither the NETA book, nor the test, cover conductor sizing.
    Reminder that our inspections and testing requirements are referenced from multiple standards beyond the NETA manuals. UL, NEMA and NEC are huge references for many LV test questions.

    NEC Sec. 445.13
    (A) General. The ampacity of the conductors from the generator output terminals to the first distribution device(s) containing overcurrent protection shall not be less than 115 percent of the nameplate current rating of the generator. It shall be permitted to size the neutral conductors in accordance with 220.61.

  6. #4
  7. Kalbi_Rob's Avatar
    Kalbi_Rob is offline Experienced Member Pro Subscriber
    Join Date
    Feb 2018
    Location
    Jacksonville, NC
    Posts
    290
    Reputation
    Quote Originally Posted by JoelHolland View Post
    "The conductor ampacity from the Generator terminals to the first distribution devices containing an overcurrent device must not be less than _____ of the generator nameplate current rating."
    Neither the NETA book, nor the test, cover conductor sizing.
    Here is a list of all standards and study material covered by the various NETA exams:

    https://higherlogicdownload.s3.amazo...st_9_19_17.pdf

Subscribe

Share this thread

Related Topics

  1. Cleaning Generator Windings
    By sparky2005 in forum NETA Level 3 Exam
    Replies: 3
    Last Post: December 8, 2021, 03:08 PM
  2. Labeling conductor in relay/ct/scada cabinets
    By prime_mover in forum Electrical Testing Talk
    Replies: 0
    Last Post: May 4, 2021, 11:43 AM
  3. Maximum size conductor for 200A load break elbow
    By J2019L in forum NETA Level 3 Exam
    Replies: 1
    Last Post: March 30, 2019, 03:22 PM
  4. What would cause a generator to trip on 32R?
    By djohnson18 in forum NETA Level 3 Exam
    Replies: 4
    Last Post: January 10, 2019, 11:28 AM
  5. Sizing equipment grounding conductors for voltage drop
    By testguy in forum Electrical Testing Talk
    Replies: 0
    Last Post: August 14, 2016, 05:04 PM

Tags for this Thread

Follow us


Explore TestGuy


NETA Certification Training


NICET Electrical Power Testing


Help and Support




You are viewing the archives. Enjoy new features and join the conversation at wiki.testguy.net