Cast core dry type GSU. 44KV/6.6KV. Tested two identical units and both had these numbers or worse. Been sitting deenergized since last November. Fans and heaters don't work, unsurprisingly. Tested again after the units had the doors off and a chance to breathe fresh air and the numbers dropped to around ~9 or so. Brought in external heaters to dry them out but I won't be able to go back for testing, unfortunately. I'll ask the crew to keep me updated, if they test again. Engineering is actually okay with the second set of results not posted here.
Both units have core ground issues as well. Engineering wants to fix the core ground issue before energizing. In a quick search, we found a black magic marker that was burned up, probably from the late 90's on one core and a 3/4 nut on the other core. Still didn't fix the core ground issue. No telling what the guys will find next week!