Follow Us
Results 1 to 1 of 1

Line Sectionalizer Exam Question

    #1
  1. bec51392 is offline NETA Level III Pro Subscriber
    Join Date
    Dec 2019
    Location
    Richmond VA
    Posts
    51
    Reputation

    Line Sectionalizer Exam Question

    First I should say I've never messed with one of these. So I looked it up in the MTS. I went to section 7.24.1 is that the proper section? Because when I go to that section, under 7.24.1.B.10 it refers me to table 100.19. Obviously the question below says table 100.16 which IS labeled "High-Potential Test Voltagefor Periodic Test of Line Sectionalizers"

    What is the NETA-MTS recommended test voltage for a 15 minute withstand test on a single-phase, 27kV line sectionalizer with a rated impulse withstand voltage of 125kV?

    Correct Answer: 78kVDC
    Help: NETA MTS-2019 Table 100.16

    I've come across similar conundrums while looking for VLF test voltages. There is a table in the back of the ATS/MTS but its never addressed as the proper table to use.

Subscribe

Share this thread

Related Topics

  1. What is the line current of this transformer?
    By mattj77 in forum NETA Level 3 Exam
    Replies: 2
    Last Post: September 23, 2022, 03:23 PM
  2. Transmission Line Fault Question
    By Jtmc78 in forum NETA Level 4 Exam
    Replies: 2
    Last Post: January 15, 2021, 10:26 AM
  3. Isolating Line protection
    By Js20981 in forum P&C / Relay Testing Talk
    Replies: 1
    Last Post: November 2, 2020, 10:02 AM
  4. Electrical Single Line Question
    By Joshua122042 in forum Electrical Testing Talk
    Replies: 3
    Last Post: June 27, 2019, 09:36 AM
  5. question on exam about using a hook stick
    By lawrence in forum NETA Level 3 Exam
    Replies: 0
    Last Post: August 9, 2018, 08:22 AM

Tags for this Thread

Follow us


Explore TestGuy


NETA Certification Training


NICET Electrical Power Testing


Help and Support




You are viewing the archives. Enjoy new features and join the conversation at wiki.testguy.net