Ground fault current on neutral resistor

 Jump to latest post
    #1
  1. MrBolt is offline Junior Member Pro Subscriber
    Join Date
    Oct 2018
    Posts
    8
    Reputation

    Ground fault current on neutral resistor

    A given 4160V 3-phase wye connected system is grounded by a 12 ohm resistor, what would the ground fault current be limited to? the Answer is 200A but I don't understand how?

  2. #2
  3. SecondGen's Avatar
    SecondGen is offline
    I push buttons.
    NETA Level III Pro Subscriber
    Join Date
    Jan 2014
    Location
    United States
    Posts
    508
    Reputation
    Quote Originally Posted by MrBolt View Post
    A given 4160V 3-phase wye connected system is grounded by a 12 ohm resistor, what would the ground fault current be limited to? the Answer is 200A but I don't understand how?
    What was your answer and why?

  4. #3
  5. Join Date
    Apr 2018
    Posts
    65
    Reputation
    Quote Originally Posted by MrBolt View Post
    A given 4160V 3-phase wye connected system is grounded by a 12 ohm resistor, what would the ground fault current be limited to? the Answer is 200A but I don't understand how?
    The key takeaway here is that it is a wye connected system.

  6. #4
  7. MrBolt is offline Junior Member Pro Subscriber
    Join Date
    Oct 2018
    Posts
    8
    Reputation
    Quote Originally Posted by SecondGen View Post
    What was your answer and why?
    4160/12=346.66

  8. #5
  9. Join Date
    Apr 2018
    Posts
    65
    Reputation
    Quote Originally Posted by MrBolt View Post
    4160/12=346.66
    That would be correct if it was a delta system. In a wye, you must divide by the square root of three and then your resistor.

  10. #6
  11. SecondGen's Avatar
    SecondGen is offline
    I push buttons.
    NETA Level III Pro Subscriber
    Join Date
    Jan 2014
    Location
    United States
    Posts
    508
    Reputation
    Quote Originally Posted by MrBolt View Post
    4160/12=346.66
    As others have stated, the key is to use phase to ground voltage.

  12. #7
  13. Join Date
    Jul 2020
    Location
    Washington, United State
    Posts
    44
    Reputation
    Quote Originally Posted by MrBolt View Post
    A given 4160V 3-phase wye connected system is grounded by a 12 ohm resistor, what would the ground fault current be limited to? the Answer is 200A but I don't understand how?
    4160/1.732=2401
    2401/12=200

  14. #8
  15. Join Date
    Jun 2022
    Posts
    3
    Reputation
    Quote Originally Posted by rofo42 View Post
    The key takeaway here is that it is a wye connected system.

    (4160/(root scuare 3))/12=(4160/root scuare 3)/12 = 200.1480 Amp
    i used Ohms law V=IR...... I=V/R..... this V is the voltage divided by scuare 3 because is a wye

Subscribe

Share this thread

Related Topics

  1. How to Size Transformer Neutral Resistor
    By AlexT90 in forum NETA Level 3 Exam
    Replies: 6
    Last Post: September 13, 2020, 07:18 PM
  2. Ground Fault Protection
    By Trevorvaligura in forum NETA Level 3 Exam
    Replies: 1
    Last Post: February 18, 2020, 07:12 AM
  3. Ground fault NEC 230.95
    By rynomite in forum NETA Level 3 Exam
    Replies: 3
    Last Post: August 2, 2019, 01:25 PM
  4. Neutral CT testing with ground bond
    By bwillsey88 in forum Electrical Testing Talk
    Replies: 2
    Last Post: May 18, 2017, 10:32 AM
  5. A phase-to-ground fault would primarily produce which type of current?
    By trhea@saberpower.com in forum NETA Level 3 Exam
    Replies: 6
    Last Post: January 8, 2016, 11:14 AM

Tags for this Thread

Follow us


Explore TestGuy


NETA Certification Training


NICET Electrical Power Testing


Help and Support