Originally Posted by
bec51392
Facing the High Voltage side of a three phase transformer, where is H1?
Your Answer: In the center
Correct Answer: Over the right shoulder
Help: Transformer Polarity Test Procedures - ANSI Rule of Thumb for Transformer Polarity
"The placement of the bushings in a three-phase transformer is also standardized. The high voltage bushings are arranged H3, H2, H1, and H0 from left to right when facing the transformer from the high-voltage side."
May just be because I'm sleepy but I don't understand why H1 is over my shoulder. if I'm looking at it why is it behind me.
According to IEEE 43, at what level may a PI value indicate that insulation is brittle?
Your Answer: 8
Correct Answer: 10
Indications of Brittle Motor Insulation
According to IEEE Standard 43, when the PI value exceeds 8 it may indicate insulation that is dried out and brittle to the point that it could fail mechanically as well as electrically.
Reference: NETA World Summer 2004 Tech Quiz #68
Also IEEE 43 2013 pg 17 second paragraph. 8 not 10.