Remembered NETA 2 Questions Help

 Jump to latest post
Page 3 of 5 FirstFirst 12345 LastLast
    #21
  1. Miller1085 is offline Junior Member Pro Subscriber
    Join Date
    Dec 2019
    Posts
    4
    Reputation

    NEMA 3R

    Quote Originally Posted by SecondGen View Post
    This could be b, c, or d but NEMA 4 would offer the most protection.

    https://testguy.net/content/158-NEMA...ical-Equipment

    NEMA 3R enclosures are compatible for both indoor or outdoor applications and holds the least demanding rating for outdoor use.

    NEMA 3R Characteristics:

    Protection against incidental contact with enclosed equipment
    Protection from falling dirt, rain, sleet and/or snow
    Drainage provision
    Protection against rain at a level higher than the lowest live part
    Alternate locking and latching mechanisms available

  2. #22
  3. rofo42 is offline Seasoned Member
    Join Date
    Apr 2018
    Posts
    65
    Reputation
    Quote Originally Posted by A_Powers1992 View Post
    To Whom it May Help:



    4.) Which XFMR test has the ability to magnetize the windings?

    a.) Power Factor
    b.) TTR
    c.) Excitiation
    d.) Zero sequence impedance


    Doble criteria my company uses states that a TTR test can magnetize the core, not windings. Excitation testing is to be performed before TTR for this reason.

  4. #23
  5. Join Date
    Jun 2021
    Location
    Houston,TX
    Posts
    27
    Reputation

    Thanks

    Thank you for the questions. Some of these I did not know either. More stuff to study I guess.

  6. #24
  7. Kalbi_Rob's Avatar
    Kalbi_Rob is offline Experienced Member Pro Subscriber
    Join Date
    Feb 2018
    Location
    Jacksonville, NC
    Posts
    290
    Reputation
    Quote Originally Posted by rofo42 View Post
    Doble criteria my company uses states that a TTR test can magnetize the core, not windings. Excitation testing is to be performed before TTR for this reason.
    Excerpt from FACILITIES INSTRUCTIONS, STANDARDS, AND TECHNIQUES, VOLUME 3-31, TRANSFORMER DIAGNOSTICS

    CAUTION:
    Perform the excitation test before any direct current (dc)
    tests. Excitation Current Tests should never be
    conducted after a dc test has been performed on the
    transformer. Results will be incorrect because of
    residual magnetism of the core left from the dc tests.
    DC WINDING RESISTANCE MEASUREMENT is the largest DC test performed on the transformer. TTR and IR testing does not have the same power applied to cause significant magnetism.
    My practice has always been to perform Power Factor Testing before any other test. I've had arguments with techs that NETA says to perform IR test first or perform IR first to check condition of Xfmr to prevent unnecessary tests (neither I agree are important as the above caution). I've always performed winding resistance last, since that same test set has the ability to de-mag the XFMR.

  8. #25
  9. Join Date
    Jul 2020
    Location
    Washington, United State
    Posts
    44
    Reputation
    Quote Originally Posted by SecondGen View Post
    This could be b, c, or d but NEMA 4 would offer the most protection.

    https://testguy.net/content/158-NEMA...ical-Equipment
    it will be class 4, because class 4 is IP64, class 3 is IP54, class 3R is IP14

  10. #26
  11. Join Date
    Jul 2020
    Location
    Washington, United State
    Posts
    44
    Reputation
    Quote Originally Posted by A_Powers1992 View Post
    To Whom it May Help:

    Here are some questions from my NETA 2 test that I remembered but did not know. All help is greatly appreciated! I did not pass....AGAIN. 406/410. 4 points!!! Third time is charm right? Ugh! Best of luck to you all. You're gonna need it.

    1.) What is the small notch in a fuse for?

    2.) Which has the greatest TIME difference?

    a.) Extremely inverse
    b.) Inverse

    Can't remember C and D sorry. I feel this may be a Level 3 question and I can honestly say the whole test felt littered with Level 3 questions!

    3.) If a motor and chain are present on an OLTC, once the tap is raised to the highest level and it's still giving a raise signal, what should the OLTC motor do?

    a.) motor stop, stay at raised level
    b.) motor continue til raise signal is gone
    c.) motor continue in reverse til back to neutral
    d.) motor stop, cool down

    4.) Which XFMR test has the ability to magnetize the windings?

    a.) Power Factor
    b.) TTR
    c.) Excitiation
    d.) Zero sequence impedance

    I would usually say Winding Resistance but it was not one of my choices.

    5.) A Multimeter is device that:

    a.) is connected in series, low impedance
    b.) is connected in series, high impedance
    c.) is connected parallel, low impedance
    d.) is connected parallel, high impedance

    6.) What is the highest pickup for a low voltage-480 system ground?

    a.) 600 A
    b.) 800 A
    c.) 1000 A
    d.) 1200 A

    7.) Why do an insulation test between neutral and ground?

    I read this and was confused on the wording. Are you talking service entrance or non service entrance? The question did not specify! Come on NETA. Killin me smalls....

    8.) Interlock on MV MCC between switch and contactor. Why?

    9.) What is the role of a VFD?

    Watch for this one. The wording in the answers was VERY confusing.

    10.) Testing motor circuits would best be achieved by use of?

    a.) Ohmmeter
    b.) Phase-angle meter
    c.) Ammeter
    d.) ???

    And no, insulation test set was not a choice.

    11.) What is the standard for testing UPS Batteries?

    99% sure it is IEEE 450,1108, 1186. But what do I know??

    12.) What are considered Network Protectors?

    13.) You arrive to find a MV circuit breaker open. At the control panel in the adjacent room you see the mechanical switch open with a red flag. What would this indicate?

    a.) The breaker lost control power
    b.) The breaker was opened at the control panel

    I cant remember C and D, I'm sorry!! Throw out common sense, because they clearly arent looking for that in one of their answers.

    14.) What is the outdoor panel class?

    a.) Class 2
    b.) Class 3
    c.) Class 3R
    4.) Class 4

    15.) How can you recognize the difference between fiber optic cables and insulated cables?

    16.) What type of swtich is best used for commercial/light industrial services rated 2000/4000 A?

    a.) safety switch
    b.) metal enclosed interrupter
    c.) bolted-pressure switch
    d.) ??

    I remembered 50 questions but these are the ones I recall taking the most time on when taking the test. Again, I hope this helps anyone preparing for their upcoming test and I hope someone may be able to assist in answering some of these items!

    Thank you in advance and good luck to future test takers!!

    AP
    2.) Which has the greatest TIME difference?

    answer is a.) Extremely inverse

  12. #27
  13. Join Date
    Jul 2020
    Location
    Washington, United State
    Posts
    44
    Reputation
    Quote Originally Posted by A_Powers1992 View Post
    To Whom it May Help:

    Here are some questions from my NETA 2 test that I remembered but did not know. All help is greatly appreciated! I did not pass....AGAIN. 406/410. 4 points!!! Third time is charm right? Ugh! Best of luck to you all. You're gonna need it.

    1.) What is the small notch in a fuse for?

    2.) Which has the greatest TIME difference?

    a.) Extremely inverse
    b.) Inverse

    Can't remember C and D sorry. I feel this may be a Level 3 question and I can honestly say the whole test felt littered with Level 3 questions!

    3.) If a motor and chain are present on an OLTC, once the tap is raised to the highest level and it's still giving a raise signal, what should the OLTC motor do?

    a.) motor stop, stay at raised level
    b.) motor continue til raise signal is gone
    c.) motor continue in reverse til back to neutral
    d.) motor stop, cool down

    4.) Which XFMR test has the ability to magnetize the windings?

    a.) Power Factor
    b.) TTR
    c.) Excitiation
    d.) Zero sequence impedance

    I would usually say Winding Resistance but it was not one of my choices.

    5.) A Multimeter is device that:

    a.) is connected in series, low impedance
    b.) is connected in series, high impedance
    c.) is connected parallel, low impedance
    d.) is connected parallel, high impedance

    6.) What is the highest pickup for a low voltage-480 system ground?

    a.) 600 A
    b.) 800 A
    c.) 1000 A
    d.) 1200 A

    7.) Why do an insulation test between neutral and ground?

    I read this and was confused on the wording. Are you talking service entrance or non service entrance? The question did not specify! Come on NETA. Killin me smalls....

    8.) Interlock on MV MCC between switch and contactor. Why?

    9.) What is the role of a VFD?

    Watch for this one. The wording in the answers was VERY confusing.

    10.) Testing motor circuits would best be achieved by use of?

    a.) Ohmmeter
    b.) Phase-angle meter
    c.) Ammeter
    d.) ???

    And no, insulation test set was not a choice.

    11.) What is the standard for testing UPS Batteries?

    99% sure it is IEEE 450,1108, 1186. But what do I know??

    12.) What are considered Network Protectors?

    13.) You arrive to find a MV circuit breaker open. At the control panel in the adjacent room you see the mechanical switch open with a red flag. What would this indicate?

    a.) The breaker lost control power
    b.) The breaker was opened at the control panel

    I cant remember C and D, I'm sorry!! Throw out common sense, because they clearly arent looking for that in one of their answers.

    14.) What is the outdoor panel class?

    a.) Class 2
    b.) Class 3
    c.) Class 3R
    4.) Class 4

    15.) How can you recognize the difference between fiber optic cables and insulated cables?

    16.) What type of swtich is best used for commercial/light industrial services rated 2000/4000 A?

    a.) safety switch
    b.) metal enclosed interrupter
    c.) bolted-pressure switch
    d.) ??

    I remembered 50 questions but these are the ones I recall taking the most time on when taking the test. Again, I hope this helps anyone preparing for their upcoming test and I hope someone may be able to assist in answering some of these items!

    Thank you in advance and good luck to future test takers!!

    AP
    5.) A Multimeter is device that:

    a.) is connected in series, low impedance
    b.) is connected in series, high impedance
    c.) is connected parallel, low impedance
    d.) is connected parallel, high impedance
    answer is d

  14. #28
  15. Join Date
    Jul 2020
    Location
    Washington, United State
    Posts
    44
    Reputation
    Quote Originally Posted by A_Powers1992 View Post
    To Whom it May Help:

    Here are some questions from my NETA 2 test that I remembered but did not know. All help is greatly appreciated! I did not pass....AGAIN. 406/410. 4 points!!! Third time is charm right? Ugh! Best of luck to you all. You're gonna need it.

    1.) What is the small notch in a fuse for?

    2.) Which has the greatest TIME difference?

    a.) Extremely inverse
    b.) Inverse

    Can't remember C and D sorry. I feel this may be a Level 3 question and I can honestly say the whole test felt littered with Level 3 questions!

    3.) If a motor and chain are present on an OLTC, once the tap is raised to the highest level and it's still giving a raise signal, what should the OLTC motor do?

    a.) motor stop, stay at raised level
    b.) motor continue til raise signal is gone
    c.) motor continue in reverse til back to neutral
    d.) motor stop, cool down

    4.) Which XFMR test has the ability to magnetize the windings?

    a.) Power Factor
    b.) TTR
    c.) Excitiation
    d.) Zero sequence impedance

    I would usually say Winding Resistance but it was not one of my choices.

    5.) A Multimeter is device that:

    a.) is connected in series, low impedance
    b.) is connected in series, high impedance
    c.) is connected parallel, low impedance
    d.) is connected parallel, high impedance

    6.) What is the highest pickup for a low voltage-480 system ground?

    a.) 600 A
    b.) 800 A
    c.) 1000 A
    d.) 1200 A

    7.) Why do an insulation test between neutral and ground?

    I read this and was confused on the wording. Are you talking service entrance or non service entrance? The question did not specify! Come on NETA. Killin me smalls....

    8.) Interlock on MV MCC between switch and contactor. Why?

    9.) What is the role of a VFD?

    Watch for this one. The wording in the answers was VERY confusing.

    10.) Testing motor circuits would best be achieved by use of?

    a.) Ohmmeter
    b.) Phase-angle meter
    c.) Ammeter
    d.) ???

    And no, insulation test set was not a choice.

    11.) What is the standard for testing UPS Batteries?

    99% sure it is IEEE 450,1108, 1186. But what do I know??

    12.) What are considered Network Protectors?

    13.) You arrive to find a MV circuit breaker open. At the control panel in the adjacent room you see the mechanical switch open with a red flag. What would this indicate?

    a.) The breaker lost control power
    b.) The breaker was opened at the control panel

    I cant remember C and D, I'm sorry!! Throw out common sense, because they clearly arent looking for that in one of their answers.

    14.) What is the outdoor panel class?

    a.) Class 2
    b.) Class 3
    c.) Class 3R
    4.) Class 4

    15.) How can you recognize the difference between fiber optic cables and insulated cables?

    16.) What type of swtich is best used for commercial/light industrial services rated 2000/4000 A?

    a.) safety switch
    b.) metal enclosed interrupter
    c.) bolted-pressure switch
    d.) ??

    I remembered 50 questions but these are the ones I recall taking the most time on when taking the test. Again, I hope this helps anyone preparing for their upcoming test and I hope someone may be able to assist in answering some of these items!

    Thank you in advance and good luck to future test takers!!

    AP
    10.) Testing motor circuits would best be achieved by use of?

    a.) Ohmmeter
    b.) Phase-angle meter
    c.) Ammeter
    d.) ???

    And no, insulation test set was not a choice.

    answer is a

  16. #29
  17. sleepiejak is offline Junior Member Pro Subscriber
    Join Date
    Mar 2020
    Posts
    4
    Reputation
    Quote Originally Posted by SecondGen View Post
    This is usually fairly obvious by the jacket, any guesses on answer options?
    from what ive seen out in the field so far. (getting to about 2 years) Ive only seen orange insulation as fiber. Its also kinda small and has a different termination then every other cable. the end kinda looks like a coax end to me

  18. #30
  19. Join Date
    Feb 2015
    Location
    Red Oak TX
    Posts
    26
    Reputation

    Question 1 notch in fuse

    1.) What is the small notch in a fuse for?

    Is the notch for "Rejection-type" which is represented as an "R" in the part number.

Page 3 of 5 FirstFirst 12345 LastLast
Subscribe

Share this thread

Related Topics

  1. NETA 4 Exam Questions 7/2018
    By MartyCoyne in forum NETA Level 4 Exam
    Replies: 29
    Last Post: June 22, 2022, 10:46 PM
  2. NETA 4 exam questions I am unsure about
    By mmacdonell in forum NETA Level 4 Exam
    Replies: 2
    Last Post: August 6, 2021, 07:15 AM
  3. Why so few questions for NETA 4 exam?
    By mmacdonell in forum NETA Level 4 Exam
    Replies: 3
    Last Post: February 10, 2020, 12:14 PM
  4. Challenging NETA questions after the test
    By adamstraub in forum NETA Level 3 Exam
    Replies: 1
    Last Post: October 24, 2019, 07:38 AM
  5. Couple NETA III Questions
    By jaycee91 in forum NETA Level 3 Exam
    Replies: 1
    Last Post: January 23, 2019, 01:14 PM