Jonsailor
To expand on this there are 3 phases that are connected to a motor. However, at the fuse switch the line side is jumpered over to the next 3 fuse switches that feeds to another motor. I believe this follows kirchoff law but unsure.
I'm not sure I'm understanding you correctly. Do you mean you're measuring like this? This would be completely normal.
Code:
V (incoming to switch)
O-- 14A (line side of switch)
|_____
sw1 \ \ sw2
7A --O O-- 7A (load side of switch)
M M (fan motors)
I hope this bad drawing makes sense. Basically if your line side measurement is upstream of where the jumper taps at the switch, then it will include current from the other switches. The load side measurement would include only one motor, but the line side would include that motor plus everything fed off the jumper.