Originally Posted by
tcoupekyle
We are out on a solar farm testing 35kv cable with Dead break terminations. The termination is 21.1kv rated but 35kv class. Cable is 35kv xlpe cable.
Neta says test at 44kv VLF for 35kv cable but there seems to be a gray area in the termination.
Any experience or recommendation on test voltage? Or test procedure?
When we try to test at 44kv vlf the set is arcing across the body.
So the plan as of now is to test at 22kv for 15 minutes and step the voltage to 44kv after that 15 minutes.