Dry Type Transformer Winding Failure After Energizing

 Jump to latest post
    #1
  1. Warrengarber's Avatar
    Warrengarber is offline
    If you ignore it, it will fail.
    Seasoned Member
    Join Date
    Jul 2017
    Location
    Jacksonville, FL
    Posts
    62
    Reputation

    Dry Type Transformer Winding Failure After Energizing

    We had a tech go out last week to test three 125Kva dry type transformers. He did an insulation resistance test and a TTR test on the used tap setting for each transformer. They all tested good PI above 1.0 all insulation resistance readings passed and the ratios were all within NETA specs. One of the transformers failed after it was energized. I was not there but the customer called me Saturday night and said the B phase winding was "smoked". So Monday morning I went out to the site to see what had happened. He was right you can see that the B phase winding was burnt on the bottom and it appears to have come from the middle of the winding out from the bottom. Can it be that because the megger puts out voltage but very little amperage so the test results were good but when they energized it with real current it failed? I was told that the panel this transformer feeds only had three single pole circuits in it so there could not have been much inrush. Does anyone else have any experience with this happening? I will say that the transformer were not build very well in the last photo you will see that the cable mounts are supported by flimsy plastic standoffs.

    Click image for larger version. 

Name:	IMG_6542.jpg 
Views:	4 
Size:	1.12 MB 
ID:	534Click image for larger version. 

Name:	IMG_6540.jpg 
Views:	0 
Size:	847.8 KB 
ID:	533Click image for larger version. 

Name:	IMG_6539.jpg 
Views:	1 
Size:	872.6 KB 
ID:	532
    Warren Garber
    Have a great day!

  2. #2
  3. Kalbi_Rob's Avatar
    Kalbi_Rob is offline Experienced Member Pro Subscriber
    Join Date
    Feb 2018
    Location
    Jacksonville, NC
    Posts
    290
    Reputation
    Quote Originally Posted by Warrengarber View Post
    We had a tech go out last week to test three 125Kva dry type transformers. He did an insulation resistance test and a TTR test on the used tap setting for each transformer. They all tested good PI above 1.0 all insulation resistance readings passed and the ratios were all within NETA specs. One of the transformers failed after it was energized. I was not there but the customer called me Saturday night and said the B phase winding was "smoked". So Monday morning I went out to the site to see what had happened. He was right you can see that the B phase winding was burnt on the bottom and it appears to have come from the middle of the winding out from the bottom. Can it be that because the megger puts out voltage but very little amperage so the test results were good but when they energized it with real current it failed? I was told that the panel this transformer feeds only had three single pole circuits in it so there could not have been much inrush. Does anyone else have any experience with this happening? I will say that the transformer were not build very well in the last photo you will see that the cable mounts are supported by flimsy plastic standoffs.

    Click image for larger version. 

Name:	IMG_6542.jpg 
Views:	4 
Size:	1.12 MB 
ID:	534Click image for larger version. 

Name:	IMG_6540.jpg 
Views:	0 
Size:	847.8 KB 
ID:	533Click image for larger version. 

Name:	IMG_6539.jpg 
Views:	1 
Size:	872.6 KB 
ID:	532
    Sounds like you had a similar issue:
    We had a customer call us after we finished testing, and they were starting to energize. They stated smoke was being emitted from C-phase, and temperature of the windings was double on C-phase versus the other two phases. We went out to site, and they energized the xfmr. After a few minutes, C-phase began to smoke. We performed TTR and PI test on the transformer and it passed with flying colors. It turns out, metal shavings fell into the transformer, and due to the baked insulation or paper insulation, neither ttr or pi testing could find the issue. Once the transformer was energized, the magnetic field heated up the metal slag, and caused it to start burning the insulation causing smoke. Manufacturer and customer resolved the issue without any further input from our office.

  4. #3
  5. Warrengarber's Avatar
    Warrengarber is offline
    If you ignore it, it will fail.
    Seasoned Member
    Join Date
    Jul 2017
    Location
    Jacksonville, FL
    Posts
    62
    Reputation

    Thanks for the Response

    This one smoked and then tripped the Main Breaker ground fault. The whole building went black. I will pass the information along to the contractor so they watch were the shavings go. Thank you




    Quote Originally Posted by Kalbi_Rob View Post
    Sounds like you had a similar issue:
    We had a customer call us after we finished testing, and they were starting to energize. They stated smoke was being emitted from C-phase, and temperature of the windings was double on C-phase versus the other two phases. We went out to site, and they energized the xfmr. After a few minutes, C-phase began to smoke. We performed TTR and PI test on the transformer and it passed with flying colors. It turns out, metal shavings fell into the transformer, and due to the baked insulation or paper insulation, neither ttr or pi testing could find the issue. Once the transformer was energized, the magnetic field heated up the metal slag, and caused it to start burning the insulation causing smoke. Manufacturer and customer resolved the issue without any further input from our office.
    Warren Garber
    Have a great day!

  6. #4
  7. SecondGen's Avatar
    SecondGen is offline
    I push buttons.
    NETA Level III Pro Subscriber
    Join Date
    Jan 2014
    Location
    United States
    Posts
    508
    Reputation
    Quote Originally Posted by Warrengarber View Post
    We had a tech go out last week to test three 125Kva dry type transformers. He did an insulation resistance test and a TTR test on the used tap setting for each transformer. They all tested good PI above 1.0 all insulation resistance readings passed and the ratios were all within NETA specs. One of the transformers failed after it was energized. I was not there but the customer called me Saturday night and said the B phase winding was "smoked". So Monday morning I went out to the site to see what had happened. He was right you can see that the B phase winding was burnt on the bottom and it appears to have come from the middle of the winding out from the bottom. Can it be that because the megger puts out voltage but very little amperage so the test results were good but when they energized it with real current it failed? I was told that the panel this transformer feeds only had three single pole circuits in it so there could not have been much inrush. Does anyone else have any experience with this happening? I will say that the transformer were not build very well in the last photo you will see that the cable mounts are supported by flimsy plastic standoffs.

    Click image for larger version. 

Name:	IMG_6542.jpg 
Views:	4 
Size:	1.12 MB 
ID:	534Click image for larger version. 

Name:	IMG_6540.jpg 
Views:	0 
Size:	847.8 KB 
ID:	533Click image for larger version. 

Name:	IMG_6539.jpg 
Views:	1 
Size:	872.6 KB 
ID:	532
    Is this a Square D transformer? I've had similar issues. One in particular I remember was less than 100kVA and had a PI over 1.0 on the 480 side to ground but the readings were very low. Nothing was visible but my suspicion was metal shavings down in the winding or faulty interwinding insulation. This was acceptance so my recommendation was not to energize and I think the mfg ended up replacing it.

  8. #5
  9. Warrengarber's Avatar
    Warrengarber is offline
    If you ignore it, it will fail.
    Seasoned Member
    Join Date
    Jul 2017
    Location
    Jacksonville, FL
    Posts
    62
    Reputation
    This one was a GE and the manufacture replaced it. The readings were all good when it was tested before being energized. Very cheaply made and flimsy.



    Quote Originally Posted by SecondGen View Post
    Is this a Square D transformer? I've had similar issues. One in particular I remember was less than 100kVA and had a PI over 1.0 on the 480 side to ground but the readings were very low. Nothing was visible but my suspicion was metal shavings down in the winding or faulty interwinding insulation. This was acceptance so my recommendation was not to energize and I think the mfg ended up replacing it.
    Warren Garber
    Have a great day!

  10. #6
  11. TestingProToBe is offline Junior Member Pro Subscriber
    Join Date
    Dec 2017
    Posts
    14
    Reputation
    Quote Originally Posted by Kalbi_Rob View Post
    Sounds like you had a similar issue:
    We had a customer call us after we finished testing, and they were starting to energize. They stated smoke was being emitted from C-phase, and temperature of the windings was double on C-phase versus the other two phases. We went out to site, and they energized the xfmr. After a few minutes, C-phase began to smoke. We performed TTR and PI test on the transformer and it passed with flying colors. It turns out, metal shavings fell into the transformer, and due to the baked insulation or paper insulation, neither ttr or pi testing could find the issue. Once the transformer was energized, the magnetic field heated up the metal slag, and caused it to start burning the insulation causing smoke. Manufacturer and customer resolved the issue without any further input from our office.
    This leads me to the question- what testing could have been done ahead of time to uncover the presence of metal shavings, I’ve been thinking this over a lot and all I can come up with is to apply a low voltage to the primary side and slowly ramp it up. Then maybe use some ultrasound testing to listen for crackling? This hardly feels like a conclusive approach and may end up damaging the unit anyway.
    Any thoughts?

  12. #7
  13. Kalbi_Rob's Avatar
    Kalbi_Rob is offline Experienced Member Pro Subscriber
    Join Date
    Feb 2018
    Location
    Jacksonville, NC
    Posts
    290
    Reputation
    Quote Originally Posted by TestingProToBe View Post
    This leads me to the question- what testing could have been done ahead of time to uncover the presence of metal shavings, I’ve been thinking this over a lot and all I can come up with is to apply a low voltage to the primary side and slowly ramp it up. Then maybe use some ultrasound testing to listen for crackling? This hardly feels like a conclusive approach and may end up damaging the unit anyway.
    Any thoughts?
    The insulation around the windings prevents normal insulation testing from picking up this issue. No non-destructive testing will cause the metal to heat up due to the lack of power produced to create a sufficient magnetic field. Without the magnetic field, it is impossible to cause inductive heating, or cut the lines of magnetic flux needed to identify. There is one test that I've performed once, that could be your best bet within the costs willing to be paid for by the end user. Transformer Surge tests are essentially a hi-pot for a transformer, and is not required by any standard at the moment. It is rarely ever used outside the factory due to this. I don't think it would actually produce the intended results you are looking for, but it is the closest test I know of without energizing the transformer.

    https://electrominst.com/test-technology/surge-tests/

Subscribe

Share this thread

Related Topics

  1. Transformer Winding Resistance
    By janmeinard in forum Electrical Testing Talk
    Replies: 7
    Last Post: February 10, 2022, 02:00 PM
  2. Transformer Winding Resistance
    By changeabilities in forum Electrical Testing Talk
    Replies: 12
    Last Post: March 29, 2021, 02:09 PM
  3. Dry-Type Transformer Testing
    By changeabilities in forum Electrical Testing Talk
    Replies: 8
    Last Post: May 15, 2019, 05:32 AM
  4. Tan / Delta or Power Factor Testing of Dry Type Transformer
    By mask12900 in forum Electrical Testing Talk
    Replies: 1
    Last Post: January 1, 2018, 08:41 PM
  5. TTR on K type transformer
    By tallyson71 in forum Electrical Testing Talk
    Replies: 1
    Last Post: May 25, 2015, 12:23 PM

Tags for this Thread

Follow us


Explore TestGuy


NETA Certification Training


NICET Electrical Power Testing


Help and Support




You are viewing the archives. Enjoy new features and join the conversation at wiki.testguy.net