VLF on 35kV cable won't start while one phase is connected to MV transfomer

    #1
  1. ericnessl is offline
    Political parties are not worthy of your identity.
    Junior Member Pro Subscriber
    Join Date
    Feb 2021
    Location
    Chapel Hill, NC
    Posts
    4
    Reputation

    VLF on 35kV cable won't start while one phase is connected to MV transfomer

    While conducting MV cable acceptance testing at 44kV using an HVA60, it was found that the test would not start while one of the phases was connected to the MV transformer (B phase) with the transformer load break switch open.
    All cables did fine on DC insulation resistance and the transformer passed all acceptance testing. Still, until the B phase dead breaks were lifted from the transformer, the VLF would not start in this particular instance. This was just one of approximately sixty transformers on site, so it was very unusual. The cables tested fine (VLF) once they were un-landed.
    Has anyone experienced this?

  2. #2
  3. Join Date
    May 2017
    Posts
    16
    Reputation
    Quote Originally Posted by ericnessl View Post
    While conducting MV cable acceptance testing at 44kV using an HVA60, it was found that the test would not start while one of the phases was connected to the MV transformer (B phase) with the transformer load break switch open.
    All cables did fine on DC insulation resistance and the transformer passed all acceptance testing. Still, until the B phase dead breaks were lifted from the transformer, the VLF would not start in this particular instance. This was just one of approximately sixty transformers on site, so it was very unusual. The cables tested fine (VLF) once they were un-landed.
    Has anyone experienced this?
    Have you verified complete proper operation of the transformer load break switch?

  4. #3
  5. ericnessl is offline
    Political parties are not worthy of your identity.
    Junior Member Pro Subscriber
    Join Date
    Feb 2021
    Location
    Chapel Hill, NC
    Posts
    4
    Reputation
    Quote Originally Posted by TestTech View Post
    Have you verified complete proper operation of the transformer load break switch?
    Yeah we did, and because the cables (unlanded from the B phase of that particular transformer) and the transformers all passed acceptance testing, they ended up landing all of the cables, energizing the circuit with all of the load breaks closed and immediately regretted it.

    I'll be interested to learn what a visual inspection from inside the transformer reveals.
    I suppose the lesson to the EPC is "If the cables test fine unlanded but the VLF test won't start with them landed, find the problem with the transformer before proceeding."

    Click image for larger version. 

Name:	PCS505.jpg 
Views:	4 
Size:	610.7 KB 
ID:	537

Subscribe

Share this thread

Related Topics

  1. Start button on a motor control bucket
    By J2019L in forum NETA Level 3 Exam
    Replies: 1
    Last Post: April 1, 2019, 07:36 AM
  2. Limited Approach Boundary for 35kV switchgear
    By ssaniti in forum NETA Level 3 Exam
    Replies: 4
    Last Post: February 10, 2019, 04:50 PM
  3. When to start studying for NETA Level 3?
    By kenner14 in forum NETA Level 3 Exam
    Replies: 8
    Last Post: October 21, 2018, 12:11 PM

Tags for this Thread

Follow us


Explore TestGuy


NETA Certification Training


NICET Electrical Power Testing


Help and Support




You are viewing the archives. Enjoy new features and join the conversation at wiki.testguy.net