    Testing into open breaker with line energized.

    So this is something I just thought to be pretty much standard practice. Don’t Meg cable into a breaker with an energized line side.
    Today I was asked where it says this. I was like you can’t test a component that has any part energized per NETA. But I kinda wasn’t sure.
    Anyone know where the literature is to back this up?

  2. #2
  3. tcoupekyle is offline Member Pro Subscriber
    Join Date
    Aug 2021
    Posts
    26
    Reputation
    Or maybe I’m just wrong and it’s perfectly fine.

  4. #3
  5. SecondGen's Avatar
    SecondGen is offline
    I push buttons.
    NETA Level III Pro Subscriber
    Join Date
    Jan 2014
    Location
    United States
    Posts
    508
    Reputation
    Quote Originally Posted by tcoupekyle View Post
    So this is something I just thought to be pretty much standard practice. Don’t Meg cable into a breaker with an energized line side.
    Today I was asked where it says this. I was like you can’t test a component that has any part energized per NETA. But I kinda wasn’t sure.
    Anyone know where the literature is to back this up?
    It probably goes against all modern safety practices but I've done it before in situations where I felt comfortable. Not sure NETA calls this out specifically but I doubt they would endorse the practice.

  6. #4
  7. tcoupekyle is offline Member Pro Subscriber
    Join Date
    Aug 2021
    Posts
    26
    Reputation
    Quote Originally Posted by SecondGen View Post
    It probably goes against all modern safety practices but I've done it before in situations where I felt comfortable. Not sure NETA calls this out specifically but I doubt they would endorse the practice.
    I’ve done it too… just always thought I was taking a short cut and thought it was definitely like a no no.

    But never had anyone ever ask about it in particular until today.

  8. #5
  9. SecondGen's Avatar
    SecondGen is offline
    I push buttons.
    NETA Level III Pro Subscriber
    Join Date
    Jan 2014
    Location
    United States
    Posts
    508
    Reputation
    Quote Originally Posted by tcoupekyle View Post
    I’ve done it too… just always thought I was taking a short cut and thought it was definitely like a no no.

    But never had anyone ever ask about it in particular until today.
    I suppose technically its a shortcut but one situation I remember was newly repaired cable in a LV switchgear, which had been re-energized by time we arrived to test. For whatever reason they couldn't get another outage so we made it work.

  10. #6
  11. tcoupekyle is offline Member Pro Subscriber
    Join Date
    Aug 2021
    Posts
    26
    Reputation
    Quote Originally Posted by SecondGen View Post
    I suppose technically its a shortcut but one situation I remember was newly repaired cable in a LV switchgear, which had been re-energized by time we arrived to test. For whatever reason they couldn't get another outage so we made it work.
    Yeah always been similar situation. On 480v or less. I don’t think I’d dare do it on anything higher voltage.

  12. #7
  13. TestingProToBe is offline Junior Member Pro Subscriber
    Join Date
    Dec 2017
    Posts
    14
    Reputation
    Quote Originally Posted by tcoupekyle View Post
    Yeah always been similar situation. On 480v or less. I don’t think I’d dare do it on anything higher voltage.
    I haven’t ever seen anything specific about not doing a test like that but it’s definitely not an ideal situation.
    And I don’t think Neta would be the place you would find that such a passage. I’d think nfpa70e might have something but they will probably just tell you about PPE required to perform that action. If you find something let us know!

  14. #8
  15. alf583 is offline Junior Member Pro Subscriber
    Join Date
    Sep 2021
    Posts
    10
    Reputation
    Quote Originally Posted by tcoupekyle View Post
    So this is something I just thought to be pretty much standard practice. Don’t Meg cable into a breaker with an energized line side.
    Today I was asked where it says this. I was like you can’t test a component that has any part energized per NETA. But I kinda wasn’t sure.
    Anyone know where the literature is to back this up?
    I don't recall seeing it in print. My company "forbids" testing with anything energized. It sounds like a common, unwritten safety practice. I'm fairly new though so I may not have come across the written rule yet.

    Like other folks said, if you're comfortable and confident then go for it. Be safe!

  16. #9
  17. JamesM is offline Junior Member Pro Subscriber
    Join Date
    Aug 2018
    Posts
    5
    Reputation
    I've done this in an old substation, we were testing single conductor cables that were terminated to a switch that was open the other side was hot at 13.8kV line.

    I was told to reduce the test voltage - AC in case we had opposing wave forms. I forget the test voltage, but I was told that if we are testing at 15kV then opposing waves (one from the test set vs system voltage) could be approx. 23kV across the switch.

    It may be that the insulation, in this case air, might not be enough to handle the extra voltage.

    - as a caveat, I was very new to testing at the time and acted under the advice of my superiors.

  18. #10
  19. Join Date
    Oct 2020
    Posts
    6
    Reputation
    Quote Originally Posted by tcoupekyle View Post
    So this is something I just thought to be pretty much standard practice. Don’t Meg cable into a breaker with an energized line side.
    Today I was asked where it says this. I was like you can’t test a component that has any part energized per NETA. But I kinda wasn’t sure.
    Anyone know where the literature is to back this up?
    Reading Megger/AVO's "A Stitch in Time", they say to not test energized equipment and one side of a switch, breaker, etc being energized and you testing the other side, that should still be considered energized equipment. I imagine that the user manual for the test equipment being used probably also advises against testing into hot equipment. If the load side fuses, bus, cables, etc of said "line hot" equipment was completely disconnected and electrically isolated from the "line hot" equipment in addition to the control device itself being open and locked out, then I would consider that an electrically-safe work condition which is absolutely positively addressed in NFPA70E. Otherwise, it's a NO!

Page 1 of 2 12 LastLast
Subscribe

Share this thread

Related Topics

  1. Basis for 50V limit for de-energized work
    By Kalbi_Rob in forum Safety and Arc Flash Talk
    Replies: 5
    Last Post: July 10, 2021, 07:21 PM
  2. Keep this in mind when working around energized equipment
    By SecondGen in forum Safety and Arc Flash Talk
    Replies: 3
    Last Post: February 22, 2021, 02:47 PM
  3. Protection and Control / Relay Testing Forum Now Open
    By testguy in forum News and Announcements
    Replies: 0
    Last Post: July 6, 2018, 02:13 PM
  4. Replies: 2
    Last Post: May 20, 2018, 08:15 AM

Tags for this Thread

Follow us


Explore TestGuy


NETA Certification Training


NICET Electrical Power Testing


Help and Support




You are viewing the archives. Enjoy new features and join the conversation at wiki.testguy.net