I think ya'll have a slight conceptual misunderstanding of how transducers work. Transducer typically output range of 4mA to 20mA. That means 4mA equals the low range minimum, and 20mA is high range maximum. For a 0-150A CT, 4mA is equal to 0A and 20mA is equal to 150A.
So, I've always just made my range 0mA to 16mA, with my reading minus 4.
So, at 14mA, my calculation would be (10mA*150A)/16mA = 93.75, so my guess would be the answer of 90A due the possibility of inaccurate.
Not sure if this question is the best example to work off of, did you get this from the question bank? Might be one to bring up to the administrators.
To check my work I use calculators similar to this one:
https://www.sensorsone.com/4-20ma-to...&olo=0&ohi=150