Follow Us
Page 2 of 2 FirstFirst 12
Results 11 to 18 of 18

Am I missing something here? Is the right answer here? If so can someone explain?

 Jump to latest post
Page 2 of 2 FirstFirst 12
    #11
  1. Join Date
    Jun 2021
    Location
    Houston,TX
    Posts
    27
    Reputation

    That's what I thought

    I was trying it the way you described because that's what I had been taught. And like we have figured out it is not an answer choice. And yes it was from the pool of questions in my NETA 2 Practice Test. Unfortunately I think the question is ignoring the 4-20mA and treating it like a 0-20mA because of the answer choices available.

    Quote Originally Posted by Kalbi_Rob View Post
    I think ya'll have a slight conceptual misunderstanding of how transducers work. Transducer typically output range of 4mA to 20mA. That means 4mA equals the low range minimum, and 20mA is high range maximum. For a 0-150A CT, 4mA is equal to 0A and 20mA is equal to 150A.

    So, I've always just made my range 0mA to 16mA, with my reading minus 4.

    So, at 14mA, my calculation would be (10mA*150A)/16mA = 93.75, so my guess would be the answer of 90A due the possibility of inaccurate.

    Not sure if this question is the best example to work off of, did you get this from the question bank? Might be one to bring up to the administrators.

    To check my work I use calculators similar to this one:

    https://www.sensorsone.com/4-20ma-to...&olo=0&ohi=150

  2. #12
  3. Join Date
    Jul 2020
    Location
    Washington, United State
    Posts
    44
    Reputation
    Quote Originally Posted by cnowak View Post
    I was trying it the way you described because that's what I had been taught. And like we have figured out it is not an answer choice. And yes it was from the pool of questions in my NETA 2 Practice Test. Unfortunately I think the question is ignoring the 4-20mA and treating it like a 0-20mA because of the answer choices available.
    same answer.

  4. #13
  5. bec51392 is offline NETA Level III Pro Subscriber
    Join Date
    Dec 2019
    Location
    Richmond VA
    Posts
    51
    Reputation
    Sooo testguy says 105 is right, are we voting this one wrong?

  6. #14
  7. testguy's Avatar
    testguy is offline Administrator Administrator
    Join Date
    Apr 2010
    Location
    United States
    Posts
    558
    Reputation
    Quote Originally Posted by bec51392 View Post
    Sooo testguy says 105 is right, are we voting this one wrong?
    Thanks for reporting, this question will be updated. See answer explination by Kalbi_Rob: https://testguy.net/threads/8410-Am-...4735#post14735

  8. #15
  9. bec51392 is offline NETA Level III Pro Subscriber
    Join Date
    Dec 2019
    Location
    Richmond VA
    Posts
    51
    Reputation
    I took my NETA 3 this week and this question ended up on my test! Thanks to you guys I think its fair to say I got it right. Thanks everyone!

  10. #16
  11. Join Date
    Feb 2015
    Location
    Red Oak TX
    Posts
    26
    Reputation

    CT ratio

    Quote Originally Posted by cnowak View Post
    A 4-20mA single CT has a max range of 150 amp what is the amps at 14mA?


    140A

    105A

    150A

    90A

    105A
    150 divided by 20 is 7.5
    That would be 7.5mA on secondary per 1 amp on primary.
    at 14mA on secondary (14 x 7.5 = 105) that would be 105 amp on primary.
    Ignore the 4 in the 4-20mA range as that is just a pickup for accuracy. Even using on 16 or 17 for the span of the range of the 4-20mA, the answer would be 123A or 131A, which is not an option, so the A per mA ratio is based on the 150 divided by 20 and ignores the lower limit of 4.

  12. #17
  13. Join Date
    Feb 2015
    Location
    Red Oak TX
    Posts
    26
    Reputation

    low limit

    Quote Originally Posted by Kalbi_Rob View Post
    I think ya'll have a slight conceptual misunderstanding of how transducers work. Transducer typically output range of 4mA to 20mA. That means 4mA equals the low range minimum, and 20mA is high range maximum. For a 0-150A CT, 4mA is equal to 0A and 20mA is equal to 150A.

    So, I've always just made my range 0mA to 16mA, with my reading minus 4.

    So, at 14mA, my calculation would be (10mA*150A)/16mA = 93.75, so my guess would be the answer of 90A due the possibility of inaccurate.

    Not sure if this question is the best example to work off of, did you get this from the question bank? Might be one to bring up to the administrators.

    To check my work I use calculators similar to this one:

    https://www.sensorsone.com/4-20ma-to...&olo=0&ohi=150

    Using that calculator with 30 as the Low Limit, it calculates the primary current to be 105A.

  14. #18
  15. Jamo33 is offline Junior Member Pro Subscriber
    Join Date
    Jun 2021
    Posts
    1
    Reputation
    Quote Originally Posted by BruceG400 View Post
    Using that calculator with 30 as the Low Limit, it calculates the primary current to be 105A.

    If this is a transducer, then at 0 amps the output will be 4mA.
    So, rather than the lower limit being 30A by calculating 150A/20mA as the max outputs, we are instead calculating 150A/(20-4) to adjust for the 4mA offset. So it is instead 150/16=9.375mA per primary Amp
    Then use this reading and multiply it by the corrected secondary reading ie (14mA-4mA)=10

    9.375*10=93.75A

Page 2 of 2 FirstFirst 12
Subscribe

Share this thread

Related Topics

  1. Ground fault current on neutral resistor
    By MrBolt in forum NETA Level 2 Exam
    Replies: 7
    Last Post: August 26, 2022, 09:03 AM
  2. Can someone explain meter accuracy?
    By RGarcia in forum NETA Level 3 Exam
    Replies: 1
    Last Post: February 2, 2021, 08:13 PM

Tags for this Thread

Follow us


Explore TestGuy


NETA Certification Training


NICET Electrical Power Testing


Help and Support




You are viewing the archives. Enjoy new features and join the conversation at wiki.testguy.net