    Neutral to ground connection in a second building

    This question is incorrect and somewhat misleading. Technically the scenario described is not legal for new installs anyway per NEC 250.32 (B)(1) BUT there is an exception made for old installs... but you still cant connect the neutral...

    question reads,

    Building A is supplied with 120/240 volt single-phase power from Building B on the same property. Building B is supplied from a three-wire with two ungrounded conductors and one neutral without any metallic water pipe or other metal equipment connections to the building or equipment ground fault protection installed. The neutral conductor must:
    Your Answer: Not be connected to a grounding electrode in the second building
    Correct Answer: Be bonded to the disconnect enclosure in the second building and connected to a grounding electrode
    Help: NFPA 70-2017 Section 250.32(D) This is a misinterpretation of that code, that section of the code that DOES mention connecting the neutral only applies to things that meet 250.30(A)(1), Exception No. 2. IE a separately derived system that meets a slew of other exceptions


    250.32 Buildings or Structures Supplied by a Feeder(s) or
    Branch Circuit(s).
    (A) Grounding Electrode. Building(s) or structure(s)
    supplied by feeder(s) or branch circuit(s) shall have a grounding
    electrode or grounding electrode system installed in
    accordance with Part III of Article 250. The grounding electrode
    conductor(s) shall be connected in accordance with
    250.32(B) or (C). Where there is no existing grounding electrode,
    the grounding electrode(s) required in 250.50 shall be
    installed.
    Exception: A grounding electrode shall not be required where only a
    single branch circuit, including a multiwire branch circuit, supplies the
    building or structure and the branch circuit includes an equipment
    grounding conductor for grounding the normally non–current-carrying
    metal parts of equipment.

    (B) Grounded Systems.

    (1) Supplied by a Feeder or Branch Circuit. An equipment
    grounding conductor, as described in 250.118, shall be run
    with the supply conductors and be connected to the building
    or structure disconnecting means and to the grounding electrode(
    s). The equipment grounding conductor shall be used
    for grounding or bonding of equipment, structures, or frames
    required to be grounded or bonded. The equipment grounding
    conductor shall be sized in accordance with 250.122. Any
    installed grounded conductor shall not be connected to the
    equipment grounding conductor or to the grounding electrode(
    s).
    Exception No. 1: For installations made in compliance with previous
    editions of this Code that permitted such connection, the grounded
    conductor run with the supply to the building or structure shall be
    permitted to serve as the ground-fault return path if all of the following
    requirements continue to be met:
    (1) An equipment grounding conductor is not run with the supply to
    the building or structure.
    (2) There are no continuous metallic paths bonded to the grounding
    system in each building or structure involved.
    (3) Ground-fault protection of equipment has not been installed on
    the supply side of the feeder(s).
    If the grounded conductor is used for grounding in accordance with
    the provision of this exception, the size of the grounded conductor shall
    not be smaller than the larger of either of the following:
    (1) That required by 220.61
    (2) That required by 250.122
    Exception No. 2: If system bonding jumpers are installed in accordance
    with 250.30(A)(1), Exception No. 2, the feeder grounded circuit
    conductor at the building or structure served shall be connected to the
    equipment grounding conductors, grounding electrode conductor, and
    the enclosure for the first disconnecting means.


    (2) Supplied by Separately Derived System.
    (a) With Overcurrent Protection. If overcurrent protection
    is provided where the conductors originate, the installation
    shall comply with 250.32(B)(1).
    (b) Without Overcurrent Protection. If overcurrent protection
    is not provided where the conductors originate, the installation
    shall comply with 250.30(A). If installed, the supply-side
    bonding jumper shall be connected to the building or structure
    disconnecting means and to the grounding electrode(s).

    (C) Ungrounded Systems.

    (1) Supplied by a Feeder or Branch Circuit. An equipment
    grounding conductor, as described in 250.118, shall be installed
    with the supply conductors and be connected to the building
    or structure disconnecting means and to the grounding
    electrode(s). The grounding electrode(s) shall also be connected
    to the building or structure disconnecting means.
    (2) Supplied by a Separately Derived System.
    (a) With Overcurrent Protection. If overcurrent protection
    is provided where the conductors originate, the installation
    shall comply with (C)(1).
    (b) Without Overcurrent Protection. If overcurrent protection
    is not provided where the conductors originate, the installation
    shall comply with 250.30(B). If installed, the supply-side
    bonding jumper shall be connected to the building or structure
    disconnecting means and to the grounding electrode(s).

    (D) Disconnecting Means Located in Separate Building or
    Structure on the Same Premises. Where one or more disconnecting
    means supply one or more additional buildings or
    structures under single management, and where these disconnecting
    means are located remote from those buildings or
    structures in accordance with the provisions of 225.32, Exception
    No. 1 and No. 2, 700.12(B)(6), 701.12(B)(5), or 702.12,
    all of the following conditions shall be met:

    (1) The connection of the grounded conductor to the
    grounding electrode, to normally non–current-carrying
    metal parts of equipment, or to the equipment grounding
    conductor at a separate building or structure shall not
    be made.

    (2) An equipment grounding conductor for grounding and
    bonding any normally non–current-carrying metal parts
    of equipment, interior metal piping systems, and building
    or structural metal frames is run with the circuit conductors
    to a separate building or structure and connected to
    existing grounding electrode(s) required in Part III of
    this article, or, where there are no existing electrodes, the
    grounding electrode(s) required in Part III of this article
    shall be installed where a separate building or structure is
    supplied by more than one branch circuit.
    (3)The connection between the equipment grounding
    conductor and the grounding electrode at a separate
    building or structure shall be made in a junction box,
    panelboard, or similar enclosure located immediately
    inside or outside the separate building or structure.

Subscribe

Share this thread

Related Topics

  1. Ground fault current on neutral resistor
    By MrBolt in forum NETA Level 2 Exam
    Replies: 7
    Last Post: August 26, 2022, 09:03 AM
  2. Building fundamental knowledge of Relay Protection
    By cotton in forum P&C / Relay Testing Talk
    Replies: 16
    Last Post: April 15, 2021, 12:08 AM
  3. Transformer neutral connection
    By sahoojoge in forum Electrical Testing Talk
    Replies: 4
    Last Post: July 18, 2019, 08:57 AM
  4. Proper connection for overcurrent relay with parallel CT's
    By marvinray in forum NETA Level 4 Exam
    Replies: 12
    Last Post: October 21, 2017, 08:07 AM
  5. Neutral CT testing with ground bond
    By bwillsey88 in forum Electrical Testing Talk
    Replies: 2
    Last Post: May 18, 2017, 10:32 AM

Tags for this Thread

Follow us


Explore TestGuy


NETA Certification Training


NICET Electrical Power Testing


Help and Support




You are viewing the archives. Enjoy new features and join the conversation at wiki.testguy.net