Neta 2 practice Q any help figuring it out

    #1
  1. Robert0 is offline Junior Member Pro Subscriber
    Join Date
    Aug 2021
    Posts
    6
    Reputation

    Neta 2 practice Q any help figuring it out

    If a watt-hour meter draws 1.5 watts and 11.3 Vars from a potential transformer, and 1.88 watts and 1.8 Vars from a current transformer, the total apparent burden placed on the current transformer is?


    1.92 VA

    2.16VA

    2.60VA

    3.24VA

    4.68VA

  2. #2
  3. Kalbi_Rob's Avatar
    Kalbi_Rob is offline Experienced Member Pro Subscriber
    Join Date
    Feb 2018
    Location
    Jacksonville, NC
    Posts
    290
    Reputation
    Quote Originally Posted by Robert0 View Post
    If a watt-hour meter draws 1.5 watts and 11.3 Vars from a potential transformer, and 1.88 watts and 1.8 Vars from a current transformer, the total apparent burden placed on the current transformer is?


    1.92 VA

    2.16VA

    2.60VA

    3.24VA

    4.68VA
    https://testguy.net/threads/5940-CT-...Burden-Problem

  4. #3
  5. Robert0 is offline Junior Member Pro Subscriber
    Join Date
    Aug 2021
    Posts
    6
    Reputation

    thank you