Which would achieve a 120/69V secondary voltage?

    #1
  1. Robert0 is offline Junior Member Pro Subscriber
    Join Date
    Aug 2021
    Posts
    6
    Reputation

    Which would achieve a 120/69V secondary voltage?

    13. On a given 480/277V system, which of the following would be used to achieve a 120/69V secondary voltage?
    Your Answer: (3) 4:1 PTs connected Delta-Delta
    Correct Answer: (3) 4:1 PTs connected Wye-Wye

  2. #2
  3. nwilliams is offline Junior Member Pro Subscriber
    Join Date
    Jan 2019
    Posts
    13
    Reputation
    Quote Originally Posted by Robert0 View Post
    13. On a given 480/277V system, which of the following would be used to achieve a 120/69V secondary voltage?
    Your Answer: (3) 4:1 PTs connected Delta-Delta
    Correct Answer: (3) 4:1 PTs connected Wye-Wye
    3 PTs connected Delta-Delta with a Turns Ratio of 4:1 will get you close to the result of 120/69V but not close enough. The problem with this configuration is that the Line-to-Line voltage and Winding voltage will both be 120V. We need the Winding voltage to be 69V. You need a Wye-configuration on the secondary to achieve this. When you use 3 PTs connected Wye-Wye with a Turns Ratio of 4:1, you get a Line-to-Line voltage of 120V and a winding voltage (can be called Line-to-Neutral in a wye configuration) of 69V.


    If you see a system described in terms of 2 voltages like 120/69V, it's likely a a wye configuration. You can check this by dividing the smaller voltage into the bigger voltage. The result will be 1.732...

    If only one voltage is given, odds are it's a delta.

  4. #3
  5. Kalbi_Rob's Avatar
    Kalbi_Rob is offline Experienced Member Pro Subscriber
    Join Date
    Feb 2018
    Location
    Jacksonville, NC
    Posts
    290
    Reputation
    Quote Originally Posted by Robert0 View Post
    13. On a given 480/277V system, which of the following would be used to achieve a 120/69V secondary voltage?
    Your Answer: (3) 4:1 PTs connected Delta-Delta
    Correct Answer: (3) 4:1 PTs connected Wye-Wye
    Acronym WiDe works really well here. For Wye configuration current (I) is equal between phase and line. For Delta configuration voltage (E) (Electromotive force, which is measured in Volts (V)) is equal between phase and line. (phase to ground and line to line)
    For Wye configuration, Line Voltage = sqrt (3) * Phase Voltage (ex: Line Voltage = 277 * 1.732 = 480)
    For Delta configuration, Line Current = sqrt (3) * Phase Current

    sqrt(3) ~ 1.732

Subscribe

Share this thread

Related Topics

  1. Wye-delta transformer secondary line current
    By RGarcia in forum NETA Level 2 Exam
    Replies: 4
    Last Post: November 7, 2021, 08:41 PM
  2. Eaton Magnum DS secondary block pin/socket type
    By bec51392 in forum Electrical Testing Talk
    Replies: 4
    Last Post: October 28, 2021, 12:00 PM
  3. Here's why you should always short a CT secondary
    By SecondGen in forum Safety and Arc Flash Talk
    Replies: 8
    Last Post: January 31, 2021, 10:26 AM
  4. Contact resistance test producing CT secondary current
    By alexlounsbury in forum P&C / Relay Testing Talk
    Replies: 9
    Last Post: November 20, 2019, 06:21 PM
  5. Overpotential test voltage for low-voltage switchgear
    By AlexT90 in forum Electrical Testing Talk
    Replies: 6
    Last Post: March 18, 2018, 08:29 PM
Follow us


Explore TestGuy


NETA Certification Training


NICET Electrical Power Testing


Help and Support




You are viewing the archives. Enjoy new features and join the conversation at wiki.testguy.net