    Transformer Insulation Resistance Test Voltages

    I've got a question regarding which DC test voltages to use for dry type power transformers. I do the standard IR tests for transformers, i.e., high to low, high to ground with low guarded, and low to ground with high guarded. NETA MTS-2019 Table 100.5 prescribes a DC test voltage based off of the transformer rating, e.g., 5kV transformer means a 2.5kV test voltage. The trouble is that the high and low side windings have different ratings, do they not? A step-down transformer may be rated 4160V on the high side but 480/277V on the low side. So for a high to low test, which DC test voltage is the appropriate one since windings of different ratings are being energized? Table 100.5 says to apply 2.5kV to a 5kV rated transformer and 1kV to a 600V rated transformer. But if the high side hypothetically was 5kV and the low side was 600V would the appropriate test voltage for a high to low test be 2.5kV or 1kV? I've searched high and low for a definitive answer.

    My understanding is that it must be 2.5kV because testing high to low is akin to testing multiple resistances in series, i.e., the resin that covers the windings and the paper. If the insulation covering the 5kV rated high side windings can withstand a test at 2.5kV, then surely the insulation of the 5kV high side AND the insulation of the 600V low side, in series, can withstand a test at 2.5kV.

    Click image for larger version. 

Name:	Screenshot_20220415-171608~2.png 
Views:	6 
Size:	179.0 KB 
ID:	586
    Last edited by michaellabeit; April 15, 2022 at 05:31 PM. Reason: adding picture

  2. #2
  3. nwilkening is offline Junior Member Pro Subscriber
    Join Date
    Feb 2016
    Posts
    2
    Reputation
    At the company I work for, when we test from high to low and high to ground we use the voltage associated with the high side of the transformer, and when we test from low to ground we use the voltage associated with the low side of the transformer.

  4. #3
  5. Join Date
    Apr 2018
    Posts
    1
    Reputation

    XFMR Insulation Resistance Testing

    The insulation system between the high and low voltage windings should be tested at the value of the higher voltage winding.

  6. #4
  7. Join Date
    Jan 2021
    Posts
    1
    Reputation
    When you do high to low, test at the high side rating (same with high to ground), and when you do low to ground, use the low side rating.

Subscribe

Share this thread

Related Topics

  1. Test Voltages used
    By merjer2005 in forum NETA Level 2 Exam
    Replies: 1
    Last Post: September 13, 2020, 06:56 PM
  2. Insulation resistance test set question
    By mkennedyShermco in forum NETA Level 4 Exam
    Replies: 2
    Last Post: June 10, 2018, 12:52 PM
  3. how to perform insulation resistance test on three phase transformer
    By mask12900 in forum Electrical Testing Talk
    Replies: 1
    Last Post: February 1, 2018, 07:15 PM
  4. 230kV Auto-Transformer (Insulation Resistance Test)
    By rizza_gay in forum Electrical Testing Talk
    Replies: 8
    Last Post: January 19, 2018, 11:27 AM
  5. Replies: 6
    Last Post: January 5, 2016, 02:09 PM

Tags for this Thread

Follow us


Explore TestGuy


NETA Certification Training


NICET Electrical Power Testing


Help and Support




You are viewing the archives. Enjoy new features and join the conversation at wiki.testguy.net