    Quote Originally Posted by Tseppish View Post
    During a saturation test of a 1500/5 multi-ratio CT, 400 volts is applied to the X1 to X4 tap. The X1 to X4 tap is the 1200/5 ratio. What is the expected voltage across the X1 to X5 tap?

    Correct answer is 0 Volts.

    Can we have clarification on what the question is suggesting? Are you applying 440 V directly on the taps? Aren't the X4 and X5 taps the same point, electrically, and would therefore have the same potential voltage?
    My initial reaction was that the answer would be correct, but after drawing it out, now I am not so sure. I would definitely not say that it's the same point electrically, because we are dealing with AC as oppose to DC, so the fact that the coil of wire acts similar to a resistor with AC, it would be reasonable to have a difference in voltage of some kind. If they were the same point electrically, then you could say the same about X1 and X4, really.

    Now, I am actually surprised that the voltage would not be higher than what was injected, because I would assume the CT to essentially act as an auto transformer, since it is one continuous piece of wire. Also, some other comments mentioned that they even tried it, and was able to read a voltage, so my instinct says the answer is wrong, but I am willing to be convinced otherwise.

  2. #12
  3. RabbleRabble is offline Member Pro Subscriber
    Join Date
    Apr 2020
    Posts
    28
    Reputation
    Quote Originally Posted by nscdrgs View Post
    The 0V is the correct answer.
    The CT is not like an "autotransformer". The circuit is closing thru x1-x4. There is no current flowing on X5. So zero current = zero voltage.
    If you take a voltage measurement across an open switch you will read line voltage. There isn’t any current flowing in an open switch. Current is dependent on voltage. Voltage is not dependent on current. The excited core of the CT induces a voltage in the windings between 4 and 5 that would be additive in this situation.

Page 2 of 2 FirstFirst 12
Subscribe

Share this thread

Related Topics

  1. What is the turns ratio?
    By franko26 in forum NETA Level 2 Exam
    Replies: 23
    Last Post: February 14, 2022, 10:36 AM
  2. Problem running ratio test with Megger multitap CT test set
    By ejbrewer in forum Electrical Testing Talk
    Replies: 5
    Last Post: June 30, 2016, 03:13 AM

Tags for this Thread

Follow us


Explore TestGuy


NETA Certification Training


NICET Electrical Power Testing


Help and Support




You are viewing the archives. Enjoy new features and join the conversation at wiki.testguy.net