    During a saturation test of a 1500/5 multi-ratio CT, 400 volts is applied to the X1 to X4 tap. The X1 to X4 tap is the 1200/5 ratio. What is the expected voltage across the X1 to X5 tap?

    Correct answer is 0 Volts.

    Can we have clarification on what the question is suggesting? Are you applying 440 V directly on the taps? Aren't the X4 and X5 taps the same point, electrically, and would therefore have the same potential voltage?

  2. #2
  3. Join Date
    Mar 2016
    Posts
    3
    Reputation
    Quote Originally Posted by Tseppish View Post
    During a saturation test of a 1500/5 multi-ratio CT, 400 volts is applied to the X1 to X4 tap. The X1 to X4 tap is the 1200/5 ratio. What is the expected voltage across the X1 to X5 tap?

    Correct answer is 0 Volts.

    Can we have clarification on what the question is suggesting? Are you applying 440 V directly on the taps? Aren't the X4 and X5 taps the same point, electrically, and would therefore have the same potential voltage?
    The 0V is the correct answer.
    The CT is not like an "autotransformer". The circuit is closing thru x1-x4. There is no current flowing on X5. So zero current = zero voltage.

  4. #3
  5. SecondGen's Avatar
    SecondGen is offline
    I push buttons.
    NETA Level III Pro Subscriber
    Join Date
    Jan 2014
    Location
    United States
    Posts
    508
    Reputation
    Quote Originally Posted by nscdrgs View Post
    The 0V is the correct answer.
    The CT is not like an "autotransformer". The circuit is closing thru x1-x4. There is no current flowing on X5. So zero current = zero voltage.
    Agreed. This question has kind of tricky wording.

  6. #4
  7. Join Date
    Mar 2017
    Posts
    2
    Reputation

    During saturation test, Multi-tap CT is an autotransformer

    Quote Originally Posted by SecondGen View Post
    Agreed. This question has kind of tricky wording.
    The voltage across X1-X5 in the condition described will be 500V. 1500/1200 X 400 = 500

  8. #5
  9. Join Date
    Apr 2017
    Posts
    15
    Reputation

    CT Testing

    Quote Originally Posted by Tseppish View Post
    During a saturation test of a 1500/5 multi-ratio CT, 400 volts is applied to the X1 to X4 tap. The X1 to X4 tap is the 1200/5 ratio. What is the expected voltage across the X1 to X5 tap?

    Correct answer is 0 Volts.

    Can we have clarification on what the question is suggesting? Are you applying 440 V directly on the taps? Aren't the X4 and X5 taps the same point, electrically, and would therefore have the same potential voltage?
    Attached Files Attached Files

  10. #6
  11. Join Date
    May 2017
    Posts
    3
    Reputation
    Quote Originally Posted by nscdrgs View Post
    The 0V is the correct answer.
    The CT is not like an "autotransformer". The circuit is closing thru x1-x4. There is no current flowing on X5. So zero current = zero voltage.
    I don't follow? If you have voltage applied across terminals 1 and 4 of an autotransformer winding, even if there is no current flowing at terminal 5 you would still measure a boosted voltage.

    What is different about a CT winding?

  12. #7
  13. Join Date
    May 2017
    Posts
    3
    Reputation
    I actually tried this because it didn't make sense to me:

    200/400/600:5 CT.

    I applied 5VAC to X1 and X2 and got 15VAC between X1 and X4, just like you would expect on any multitap winding.

    Maybe I'm missing something, but it appears that test answer is incorrect.

  14. #8
  15. Join Date
    Feb 2019
    Posts
    1
    Reputation

    500V is the answer

    GPerske and BigJohn are correct.
    The entire length of the coil is one continuous wire. Therefore regardless of where you stab into the taps with your test voltage, voltage will exist on the entire coil and will be boosted beyond the test points, all the way to each end of the coil.
    1500/1200x400=500.

  16. #9
  17. Join Date
    Dec 2019
    Posts
    1
    Reputation

    Greetings

    I'm helping a friend study for an introduction to motor controls class. They have been really confused about calculating multi-tap on a CT. If a test voltage is applied X1 and X2 what would be the test on the subsequent x4 and x5 taps? Any help would be greatly appreciated!

  18. #10
  19. Join Date
    Nov 2019
    Posts
    16
    Reputation
    Quote Originally Posted by bertywho105 View Post
    I'm helping a friend study for an introduction to motor controls class. They have been really confused about calculating multi-tap on a CT. If a test voltage is applied X1 and X2 what would be the test on the subsequent x4 and x5 taps? Any help would be greatly appreciated!
    You need the ANSI "C" class number (C800, C400, etc) to determine. You can google ANSI C400 and get a graph showing the kneepoint voltages for all tap combinations.

Page 1 of 2 12 LastLast
Subscribe

Share this thread

Related Topics

  1. What is the turns ratio?
    By franko26 in forum NETA Level 2 Exam
    Replies: 23
    Last Post: February 14, 2022, 10:36 AM
  2. Problem running ratio test with Megger multitap CT test set
    By ejbrewer in forum Electrical Testing Talk
    Replies: 5
    Last Post: June 30, 2016, 03:13 AM

Tags for this Thread

Follow us


Explore TestGuy


NETA Certification Training


NICET Electrical Power Testing


Help and Support




You are viewing the archives. Enjoy new features and join the conversation at wiki.testguy.net