Originally Posted by
EricGoetz92
Negative sequence current increases as the current imbalance rises, but zero sequence doesn't necessarily increase. You are correct in saying that negative sequence current occurs for a reverse rotation, but it is kind of assumed that you wouldn't just magically get a reverse rotation on a generator after it is has been running for a while. Reverse rotation detection (paired with a sync check relay) is more a permissive to close than "running" protection. However, you can have an unbalanced load without having zero sequence current depending on the nature of the unbalance. For example, let's say the generator is supplying a wye connected motor that is protected by a fused contactor. If the C phase fuse blows and the motor starts to single phase, all of the current entering A phase is leaving B phase offset by 180 degrees. So there is no zero sequence component to it (since there is no ground current), but there is an increase in the negative sequence current.