Low Voltage CB Short time pick up tolerance..?

    #1
  1. Isaiah is offline
    kikapoo
    Junior Member Pro Subscriber
    Join Date
    Jul 2021
    Posts
    5
    Reputation

    Low Voltage CB Short time pick up tolerance..?

    Hi Guys,

    So recently I came into a dilemma, there was testing being done on a low voltage cb with a micrologic 6.0P LSI the breaker's frame and trip rating is 800A the short time pick-up was set at 1.5 (min). so in that sense the pick up should be 1,200A. Now once I was doing revision on the data sheets i noticed test results as low as 840A-1000A for the short time pick up! it just feels wrong but when asked for a source i couldnt find any sources or tolerances stating that the short time pick up test results should be within a certain tolerance like IT has our NETA tables. Any help please in knowing if there is a such thing as a tolerance threshold for short time pickup? thanks sorry for the long explanation

  2. #2
  3. Kalbi_Rob's Avatar
    Kalbi_Rob is offline Experienced Member Pro Subscriber
    Join Date
    Feb 2018
    Location
    Jacksonville, NC
    Posts
    290
    Reputation
    Quote Originally Posted by Isaiah View Post
    Hi Guys,

    So recently I came into a dilemma, there was testing being done on a low voltage cb with a micrologic 6.0P LSI the breaker's frame and trip rating is 800A the short time pick-up was set at 1.5 (min). so in that sense the pick up should be 1,200A. Now once I was doing revision on the data sheets i noticed test results as low as 840A-1000A for the short time pick up! it just feels wrong but when asked for a source i couldnt find any sources or tolerances stating that the short time pick up test results should be within a certain tolerance like IT has our NETA tables. Any help please in knowing if there is a such thing as a tolerance threshold for short time pickup? thanks sorry for the long explanation
    Dependent on Manufacturer specifications. Long time Pickup typically have 10% deviation, and Short time pickup is a multiple of that pickup, so it should also fall with in the same deviation specs. That being said, you also have to take into effect your own test set deviation error %. An 800A breaker should not be tripping before 1100A on a 1.5x setting. I would definitely re-verify your LT pickup and slow ramp the trip for ST pu.

    "Short-time delay and pickup. The short-time delay characteristic provides protection against short-circuit or fault conditions. An intentional delay is provided for coordination or selectivity with other protection devices. The short-time pickup is a multiple of the long-time pickup. "
    -NETAworldjournal.org https://netaworldjournal.org/primary...cuit-breakers/

  4. #3
  5. Join Date
    Dec 2021
    Posts
    2
    Reputation
    Quote Originally Posted by Isaiah View Post
    Hi Guys,

    So recently I came into a dilemma, there was testing being done on a low voltage cb with a micrologic 6.0P LSI the breaker's frame and trip rating is 800A the short time pick-up was set at 1.5 (min). so in that sense the pick up should be 1,200A. Now once I was doing revision on the data sheets i noticed test results as low as 840A-1000A for the short time pick up! it just feels wrong but when asked for a source i couldnt find any sources or tolerances stating that the short time pick up test results should be within a certain tolerance like IT has our NETA tables. Any help please in knowing if there is a such thing as a tolerance threshold for short time pickup? thanks sorry for the long explanation
    Since it is a Micrologic 6.0 (Ground Fault Equipped) were you using a secondary injection test set to defeat GF? My guess would be either the breaker picked up too low, you still had GF active, or you didn't have the thermal memory inhibited. If With that being said the STPU Threshold for a Micrologic 6.0(A/P/ETC.) is +/- 10%. A Micrologic 6.0 is a LSIG Breaker.

Subscribe

Share this thread

Related Topics

  1. Time Overcurrent Relay Time Calculator
    By changeabilities in forum Technical Documents
    Replies: 1
    Last Post: March 27, 2021, 01:04 PM
  2. Here's why you should always short a CT secondary
    By SecondGen in forum Safety and Arc Flash Talk
    Replies: 8
    Last Post: January 31, 2021, 10:26 AM
  3. Windining Resistance value Tolerance limit of dry transformer??
    By shamimkhan in forum Electrical Testing Talk
    Replies: 1
    Last Post: November 30, 2017, 09:10 AM
  4. winding resistance tolerance for a transformer test
    By Larry5441 in forum Electrical Testing Talk
    Replies: 6
    Last Post: June 29, 2015, 04:33 PM

Tags for this Thread

Follow us


Explore TestGuy


NETA Certification Training


NICET Electrical Power Testing


Help and Support




You are viewing the archives. Enjoy new features and join the conversation at wiki.testguy.net