nwilliams
IEEE 400.2 states "[w]hen a switch or disconnect type device is used to isolate the cable circuit from the rest of the system, the ability of the device to sustain the VLF ac test voltage and maintain isolation while the
other end is under normal operating voltage shall be checked with the manufacturer."
IEEE 400.2 also states, albeit in reference to Tan Delta testing, "[i]n addition, some utilities may have components connected to the cable circuit being measured, e.g., oil-filled switches, that cannot be removed but can influence the test results. Most users of dielectric response techniques choose to measure the entire cable
system response that would include the responses from all terminations, cable, and joints within the circuit."
So this is the closest I could find to what you're looking for. I hope it answers your question.