    A system with an operating voltage of 13.8 kV line-to-line utilizes a wye-connected source with a 400 ampere grounding resister. Which of the following is the most suitable rating for lighting arresters?

    a. 15kV
    b. 5kV
    c. 8kV
    d. 10kV
    e. 12kV

    The answer is 12kV, but I am unsure as to why. Can someone help me out on this?

  2. #2
  3. Donalddc is offline Junior Member Pro Subscriber
    Join Date
    May 2021
    Posts
    7
    Reputation
    Quote Originally Posted by anderssok09 View Post
    A system with an operating voltage of 13.8 kV line-to-line utilizes a wye-connected source with a 400 ampere grounding resister. Which of the following is the most suitable rating for lighting arresters?

    a. 15kV
    b. 5kV
    c. 8kV
    d. 10kV
    e. 12kV

    The answer is 12kV, but I am unsure as to why. Can someone help me out on this?
    I briefly looked this up and found the following in Testguy in "Surge Arresters: Selection, Application and Testing Overview"

    I found this in the article.

    MCOV Example 1: 13.8kV Solidy Grounded System
    The continuous operating voltage is 13,800 divided by the square root of 3, or 7970 V. This is above the MCOV of 7,650 V for an arrester rated 9 kV.

    Depending on the magnitude and duration of system overvoltages, it may be necessary to use a 10 kV arrester with an MCOV of 8.4 kV or a 12 kV arrester with an MCOV of 10.2 kV.

    MCOV Example 2: Resistance-grounded 13.8 kV system
    Depending on the time needed for protective relays to clear ground faults off the system, the choice will be between arresters rated 12 kV, 15 kV and 18 kV.

    MCOV Example 3: 13.8kV Ungrounded System
    The 12.7 kV MCOV of a 15 kV arrester is not adequate for a nominal voltage of 13.8kV. Use an 18 kV arrester with an MCOV of 15.3 kV.

    There are multiple choices in each, but your question said 400A ground resistor, so I am assuming Example 2.

    This still does not answer your question of "why" but may head you in the correct direction.

Subscribe

Share this thread

Related Topics

  1. UL Lightning Protection Journeyman Certification
    By changeabilities in forum Electrical Testing Talk
    Replies: 0
    Last Post: January 3, 2022, 10:36 PM
  2. 13.8KV Lightning Arrester
    By spdave2004 in forum Electrical Testing Talk
    Replies: 0
    Last Post: February 12, 2021, 09:50 AM
  3. Lightning Arrestor Ratings
    By breny426 in forum NETA Level 3 Exam
    Replies: 1
    Last Post: December 2, 2020, 02:55 AM
Follow us


Explore TestGuy


NETA Certification Training


NICET Electrical Power Testing


Help and Support




You are viewing the archives. Enjoy new features and join the conversation at wiki.testguy.net