Log in

View Full Version : VCB Contact Resistance



shamimkhan
December 8, 2017, 12:55 AM
We measured contact resistance of VCB (11KV), the values are as below:

Phase Applied Current Resistance
L1 100 A 17 μΩ
L2 100 A 32 μΩ
L3 100 A 23 μΩ

Please let me know whether or not the result is satisfactory ? If not why? Please give reason / standard reference.

SecondGen
December 8, 2017, 10:36 AM
We measured contact resistance of VCB (11KV), the values are as below:

Phase Applied Current Resistance
L1 100 A 17 μΩ
L2 100 A 32 μΩ
L3 100 A 23 μΩ

Please let me know whether or not the result is satisfactory ? If not why? Please give reason / standard reference.

L2 reading is a little high. Glad to see you did 100A test, each phase should be within 50% of each other per NETA standards. Going off the lowest number (17 microhms), nothing should be over 25.5 but you should consult the maintenance manual for suggested values from manufacturer.